Originally Posted by
ogoun
For the RTD, the PT100 platinum ones are quite cheap on epay, and have exceptional accuracies and (for the small ones that arent encapsulated) stunning response times. Additionally, they are the most linear direct temp measurement sensor known. Also, calibration is unnecessary, since the r versus temp is a known physical function of the dimensioning of (in this case) the Pt100 (platinum, 100 ohms) element. Apart from anything else, this means that one Pt100 sensor will to a very close tolerance, match the output of any other. There is some published standard somewhere that defines all this RTD stuff. Oh, and they are good over an incredibly wide range of temperatures.
Anyway, I think they are good ;)
Usually, an RTD has 4 wires attached, 2 for the DC current flow, and 2 (connected in parallel with the first 2 right at the RTD itself) for measuring the voltage developed across the RTD.
We could look at either a constant current source, or we could just use the supply voltage, pass it through a 1% or better series resistor, and use an A to D input to measure the current being supplied to the RTD. Then we measure the voltage across the RTD with another A to D input, do R=V/I in software, and then we have the RTD resistance, and hence the temp.
An alternative for when the RTD is close to the controller, and I2R losses in the connecting wires is negligible (this is probably the case here), is to just use 2 wires, and have a resistive divider made up of the RTD and the 1% or better series resistor. Then you AtoD the supply rail, and the RTD voltage (assuming the RTD is connected to ground), then do the rest of the calcs in software.
The upshot of all of this is that the hardware required to support RTDs is minimal, especially using the 2 wire method.
Using LM35s, and similar have a whole set of issues, calibration, linearity, resolution, temperature range, response time and thermal coupling. A little known fact is that most if not all these plastic TO92 or metal can TO15 packaged sensors do not readily couple thermally using their case!!! I was shocked to learn this too, since I have used the old TO15 can package several times, and just did what every one else did/does, i.e. clamped the can body to the surface to be measured, with some thermal grease.
In fact, the main thermal coupling mode for these sensors is via the metal leads!!
Hope this all helps...